独立安全出口必须是独立独立楼梯间吗

各位大佬,请教一个问题:丙类厂房办公室要求设置独立的安全出口,多层厂房办公室设置的独立安全出口必须是独立的楼梯间吗?换句话说,办公室的楼梯间(通向楼梯间的门是独立的)可以与生产区域共用吗?

GaleLee | 2025-04-10 18:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-04-11 08:42 00 [回复]举报

独立

LHH2737 2025-04-11 09:28 00 [回复]举报

不可以共用

李勤 2025-04-11 11:25 00 [回复]举报

不可以共用,仅自己的场所单独使用。

蒋清云 2025-04-12 11:08 10 [回复]举报

建议根据你项目情况按防火通规实施指南4.2.2条,不一定的

牛丫头消防课堂 2025-05-15 15:17 00 [回复]举报

首先你要明白这个独立的楼梯间是对办公区域而言的,也就是这个楼梯间,人员不需要经过厂房区域就能疏散。

但是厂房区域与办公区域之间墙体上可以设置用于联通的乙级门。