室内埋地消防管选择钢丝网骨架塑料复合管,可行?

mshm | 2024-10-19 17:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

懒得说 2024-10-21 10:40 00 [回复]举报

可行。已经好多个成功案例了

熬不牢一泡肚皮杂   回复: 懒得说2024-10-22 08:33

没有一个成功过

0    0 [回复]举报

溜达呀 2024-10-22 00:09 00 [回复]举报

可以的,我工作的厂区就是用的钢丝网骨架复合管。只不过对水压有要求。 还有穿过马路要做套管保护

画图匠 2024-11-07 12:12 00 [回复]举报

应该根据系统工作压力复核是否可行,如果工作压力超过1.6MPa要选用无缝钢管了