消防稳压泵的火灾报警联动控制要求

消防稳压泵的火灾报警联动控制要求是怎样的,联锁启停条件有哪些?

wangh6 | 2021-02-25 10:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防打工人 2021-02-26 14:46 50 [回复]举报

火灾报警联动控制只针对消火栓泵、喷淋泵等灭火应急供水泵。稳压泵的作用是日常维持管网压力,不通过报警系统联动控制,而是通过电接点压力表来控制,当管网压力低于电接点压力表设定的低压值时启动稳压泵,当管网压力高于电接点压力表设定的高压值时停止稳压泵。

wangh6   回复: 消防打工人2021-05-14 16:28

感谢回答

0    0 [回复]举报

李勤 2025-07-07 11:04 00 [回复]举报

稳压泵启停不靠联动关系,靠的是稳压泵上边设置的电接点压力表,通过设置上下限启停稳压泵。