总面积超过3000平方的多层办公建筑需要做喷淋吗,没有中央空调

薯条 | 2024-03-30 10:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

阳明心 2024-04-01 10:51 00 [回复]举报

不需要

南明离火 2024-04-01 10:58 00 [回复]举报

不用

安洪全 2024-04-01 12:51 00 [回复]举报

可不设

建筑防火通用规范 GB55037-2022

8.1.9 除建筑内的游泳池、浴池、溜冰场可不设置自动灭火系统外,下列民用建筑、场所和平时使用的人民防空工程应设置自动灭火系统:    

1 一类高层公共建筑及其地下、半地下室;    

2 二类高层公共建筑及其地下、半地下室中的公共活动用房、走道、办公室、旅馆的客房、可燃物品库房;    

3 建筑高度大于100m的住宅建筑;    

4 特等和甲等剧场,座位数大于1500个的乙等剧场,座位数大于2000个的会堂或礼堂,座位数大于3000个的体育馆,座位数大于5000个的体育场的室内人员休息室与器材间等;    

5 任一层建筑面积大于1500㎡或总建筑面积大于3000㎡的单、多层展览建筑、商店建筑、餐饮建筑和旅馆建筑;   

6 中型和大型幼儿园,老年人照料设施,任一层建筑面积大于1500㎡或总建筑面积大于3000㎡的单、多层病房楼、门诊楼和手术部;    

7 除本条上述规定外,设置具有送回风道(管)系统的集中空气调节系统且总建筑面积大于3000㎡的其他单、多层公共建筑;    

8 总建筑面积大于500㎡的地下或半地下商店;    

9 设置在地下或半地下、多层建筑的地上第四层及以上楼层、高层民用建筑内的歌舞娱乐放映游艺场所,设置在多层建筑第一层至第三层且楼层建筑面积大于300㎡的地上歌舞娱乐放映游艺场所;    

10 位于地下或半地下且座位数大于800个的电影院、剧场或礼堂的观众厅;    

11 建筑面积大于1000㎡且平时使用的人民防空工程。

步步高 2024-04-01 15:31 00 [回复]举报

根据《建筑防火通用规范》这种情况不用做自动喷淋灭火。

同同不同 2024-04-01 17:17 00 [回复]举报

若无送回风管道不需要