排烟风管的尺寸计算

排烟风管的主管根据计算风量或者设计风量来计算,但是支管是按该单独那个防烟分区的风量来计算还是与主管一般呢,如果是按防烟分区的风量来计算的话,风机运行的话风管是否会烧坏,且用风机的风量来计算此时支管的风管话,风管风速已经超过20m/s,时候是两处支管面积之和不超就算合格,,,,,请各位大佬指点指点。。。

殇~~ | 2021-02-01 15:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防网友9144 2021-02-01 17:36 00 [回复]举报

1、支管按防烟分区计算就行;2、风管还要满足规范对耐火极限的要求;3、风速大于20m/s,一般在支管设置调节阀。

刘丽波 2021-02-01 17:41 10 [回复]举报

排烟主管按计算风量选风管尺寸,设计风量是用来选风机的。排烟支管按防烟分区的计算风量选风管尺寸。火灾时,按防烟分区开启风口,风机的运行风量不是选定的风机风量,会自行调节。排烟风机与消防泵一样,会在各种可能风量下运行,风机不会烧毁。