如何确定一道墙体是否需要隔热?

现遇到项目,审图机构提出走道两侧的非承重墙体如需采用防火玻璃时,应当采用A类隔热型防火玻璃,不可采用C类非隔热性防火玻璃。

请问有什么条款规定了墙体的隔热性要求?

澜沐 | 2023-09-07 16:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

张治福 2023-09-07 16:51 00 [回复]举报

走道两侧的墙规范要求有耐火极限要求,其中耐火极限概念就包含了完整性、承载能力、隔热性。

澜沐   回复: 张治福2023-09-07 17:13

我明白耐火极限的概念

但是防火玻璃有区分C类防火玻璃(非隔热)和A类防火玻璃(隔热),两者都有一定的耐火极限。

但目前情况是项目采用的C类防火玻璃已满组规范要求的耐火极限时间要求,却被告知C类防火玻璃没有隔热型,这应该怎么解释。。。

0    0 [回复]举报

南明离火   回复: 澜沐2023-09-07 17:47

C类只满足耐火性,并不满足隔热性 所以仍然 不满足

0    0 [回复]举报

澜沐   回复: 南明离火2023-09-11 09:55

但《建筑防火通用规范》第6.4.9条规定上也只明说要耐火性,没有要求隔热性。到底应当如何执行?

0    0 [回复]举报

同同不同   回复: 张治福2023-09-13 09:06

非承重隔墙可不具备承载能力;

玻璃的隔热性、完整性要求应视使用场景确定;

走道一般指疏散走道,作为疏散用,会有人员经过此处疏散,必然要求既满足隔热性又满足完整性。

0    0 [回复]举报

张治福 2023-09-08 08:06 00 [回复]举报

参考一下这本规范《v建筑用安全玻璃 第1部分:防火玻璃 GB15763.1-2009》

3.6 隔热型防火玻璃(A类) insulated fire-resistant glass(A type)     耐火性能同时满足耐火完整性、耐火隔热性要求的防火玻璃。

3.7 非隔热型防火玻璃(C类) integrity-only fire-resistant glass(C type)     耐火性能仅满足耐火完整性要求的防火玻璃。



澜沐   回复: 张治福2023-09-11 09:55

但《建筑防火通用规范》第6.4.9条规定上也只明说要耐火性,没有要求隔热性。到底应当如何执行?

0    0 [回复]举报

风无心   回复: 澜沐2023-09-12 14:58

上面的大哥不是截图很清楚了吗   耐火性能不是耐火完整性的意思。

0    0 [回复]举报