低压压力开关或电接点压力表起泵的动作信号反馈到消防报警主机的规范条文在哪?一直没找到

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

牛疼 2023-07-28 10:04 00 [回复]举报

原子弹大爆炸   回复: 牛疼2023-07-28 13:33

第4.4.3只写了消火栓动作信号做反馈,低压压力开关是否需要信号反馈至消防报警主机?

0    0 [回复]举报

同同不同   回复: 原子弹大爆炸2023-07-28 14:15

消火栓泵启动信号反馈至消控室

0    0 [回复]举报

胡胡203 2023-07-28 16:56 10 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014 >13.2.17流量开关、低压压力开关和报警阀压力开关等动作,应能自动启动消防水泵及与其联锁的相关设备,并应有反馈信号显示;

原子弹大爆炸   回复: 胡胡2032023-07-28 17:32

感谢大哥,这下找到了

0    0 [回复]举报