消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

到底能不能一个消火栓按钮就联动启泵?

规范GB50116-2013里说的消火栓按钮作为启泵联动触发信号,所以认为一个消火栓按钮联动启泵到底合不合理呢?如果硬是需要与逻辑启泵规范也没有明说呀,这个争议很大啊。如果不能那么消火栓按钮作为联动触发信号这个“联动触发信号”有什么深度解答吗?

郑在忙 | 2022-07-23 13:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

充楞装傻 2022-07-23 16:45 00 [回复]举报

按新版验收规范操作~~3联动

 火灾自动报警系统施工及验收标准 GB50166-2019 >

  4.17.6  1 应使任一报警区域的两只火灾探测器,或一只火灾探测器和一只手动火灾报警按钮发出火灾报警信号,同时使消火栓按钮动作;

阿童木木 2022-07-23 17:28 00 [回复]举报

周家斌 2022-07-23 18:01 20 [回复]举报

规范很清楚

刘丽波 2022-07-23 20:25 10 [回复]举报

消火栓按钮是否启泵有水专业提给电气专业。报警规范是2013年的,消水规2014年执行,有些不协调的地方。具体以消水规12.0.19条为准。


消防黄河 2022-07-23 23:26 00 [回复]举报

按照现行规范要求,一个消火栓按钮信号不可以直接启泵。需与其他火灾信号与逻辑,确认火灾,启泵。

关闭

关闭

手机APP下载