防火玻璃能代替防火墙吗?

杜浒 | 2022-04-18 11:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

牛疼 2022-04-18 13:40 00 [回复]举报

防火墙要求至少满足3小时的耐火,防火玻璃达不到;

但是增加其他的设施或许可以达到防火墙的需求。

消防网友78337 2022-04-18 14:20 00 [回复]举报

一般不建议进行防火玻璃代替防火墙的设计,

防火墙的重力承载能力不是防火玻璃可以代替的


即使防火墙不需要考虑重力承载能力,也是一样不建议。


14年建规就限制了防火卷帘的长度,防火卷帘本身就没有承载能力。