有关于气溶胶灭火系统的最新明文规定吗

有关于气溶胶灭火系统的最新明文规定吗?给一家单位换了新的S型热气溶胶灭火装置,结果单位领导说气溶胶属于淘汰产品,不给批合同,故问问各位大佬有关于气溶胶被淘汰不能使用的明文规定吗?或者关于气溶胶灭火系统的最新信息

曰辰 | 2021-08-04 13:03
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-08-01 08:43 00 [回复]举报

以往是没有强制性认证,现在可以用了。

萌小宝   回复: 周家斌2023-12-20 10:22

周老师,客户单位一S型落地式气溶胶2012年4月的,现已超十年了,请问是建议更换其他的还是检测继续用回气溶胶呢

0    0 [回复]举报

周家斌   回复: 萌小宝2023-12-21 09:02

可以继续

0    0 [回复]举报

潘天坤 2025-06-17 14:06 00 [回复]举报

目前无禁用“热气溶胶”这款产品的规定,24年《热气溶胶灭火装置(报批稿)》还在征求意见,说明这款产品是没有被淘汰的


不过要注意下有些场所和火灾不适用,不应将热气溶胶产品设置在不适用的场所(例如制药、芯片加工等人员密集场所、有爆炸危险性的场所、有超净要求的场所)及气体灭火系统不适用的火灾(例如硝化纤维、硝酸钠等氧化剂或含氧化剂的化学制品火灾;钾、镁、钠、钛、锆、铀等活泼金属火灾;氢化钾、氢化钠等金属氢化物火灾;过氧化氢、联胺等能自行分解的化学物质火灾;可燃固体物质的深位火灾)

特别注意:除电缆隧道(夹层、井)及自备发电机房外,K型及其他型热气溶胶预制灭火系统不得用于其他电气火灾,也不得用于电子计算机房、通讯机房等场所


最后就是建规GB50016条文说明有提到气溶胶适用的一些场所:有的场所空间很大,只有部分设备是主要的火灾危险源并需要灭火保护,或建筑内只有少数面积较小的场所内的设备需要保护时,可对该局部火灾危险性大的设备采用火探管、气溶胶、超细干粉等小型自动灭火装置进行局部保护


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准