手动火灾报警装置包括什么

请问根据《烟花爆竹工程设计安全标准》 GB50161-2022

13.4.1 危险品生产区和危险品意仓库区应设置手动火灾报警装置或火灾自动报警系统。值班室的固定电话可兼作火灾报警装置。根据本条规范在不大于500平的仓库里仅设置手动火灾报警按钮,没有火灾报警控制器可以吗?

王文华 | 2025-02-18 14:45
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

潘天坤 2025-02-19 07:50 00 [回复]举报

13.4章节的标题是火灾自动报警系统,结合内容来看,讲的应该是火灾自动报警系统内的设备

结合火灾自动报警设计规范GB50116和本章节来看,手动火灾报警装置可以包括手动火灾报警按钮及固定电话,也就是说可以仅在值班室设置固定电话,或者仅设置手动火灾报警按钮,或者设置火灾自动报警系统

赖峰 2025-02-19 09:10 00 [回复]举报

‌不可以仅设置手动火灾报警按钮而没有火灾报警控制器‌。如果没有火灾报警控制器,手动火灾报警按钮就无法将火警信号传输到消防控制室或其他指定的接收点,从而无法实现其报警功能‌

王文华   回复: 赖峰2025-02-19 09:21

谢谢

0    0 [回复]举报

王文华   回复: 赖峰2025-02-19 09:22

谢谢

0    0 [回复]举报