请教各位老师3个问题

各位老师,请教政府部门检查的3个问题,规范上都没有找到相关内容,烦请各位老师指点,谢谢!
1.4层的沿街商铺,3层及以上是正面广告外立面钢架,设有消防窗,消防窗外面有标志,检查人员说消防窗里面也要有标识。
2.4层的商铺,消防楼梯间需要楼层显示标志吗?
3、消防楼梯间涉及百叶窗里面加装了铁丝网,检查人员让把铁丝网拆除。
我个人认为这3点规范都没有表明,算不上违反规定吧?

红门铠甲 | 2025-01-08 11:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-01-08 14:42 00 [回复]举报

二去商量下,别的简单赶紧改了。

红门铠甲   回复: 小唐123212025-01-08 17:29

谢谢老师的

0    0 [回复]举报

关二斤 2025-01-08 16:07 00 [回复]举报

第一个问题建筑防火通用规范2.2.3.5有讲

红门铠甲   回复: 关二斤2025-01-08 17:29

谢谢老师的

0    0 [回复]举报

jinyanwu 2025-01-09 09:46 00 [回复]举报

个人意见,仅供参考:

1、根据通规:

第5条,室内室外均应设置。

2、根据《消防应急照明和疏散指示系统技术标准 GB51309-2018》:

按照规定要求设置即可。

3、根据国家消防救援局2024年2月1日通告:

符合人员密集场所定义的拆除即可。